Slide 1: MERALCO Standards: Electrical Design
MERALCO Standards: Electrical Design Engr. Eduard Mercado Electrical Design Team
Slide 2: Electrical Design Standards
Electrical Design Standards
Slide 3: Service Voltages and Facilities
SERVICE VOLTAGES • SECONDARY METERED - 240 V, 400 V, 460 V • PRIMARY METERING -34.5 kV, 13.8 kV (portions of Cavite & Bulacan), 115 kV (Subtransmission) FACILITIES 1. OVERHEAD • POLE MOUNTED TRANSFORMERS • PADMOUNT TRANSFORMERS • VAULT TYPE DT 2. UNDERGROUND • PADMOUNT TRANSFORMERS • VAULT TYPE DT
Slide 4: Single Line Diagram: Overhead Line Feeding a Transformer Vault
Single Line INCOMING OVERHEAD LINE Diagram TERMINAL SURGE POLE ARRESTER FUSE CUTOUT OR POWER FUSE CABLE ALL CIVIL WORKS, i.e., TERMINATION CONCRETE-ENCASED PVC DUCTS & FITTINGS, TO BE UNDERGROUND PROVIDED AND INSTALLED BY PRIMARY THE APPLICANT/CUSTOMER CABLES ELBOW ARRESTER PADMOUNTED TRANSFORMER VA
Slide 5: Single Line Diagram: Underground Feeder
Single Line UNDERGROUND FEEDER Diagram PADMOUNTED SWITCHGEAR ALL CIVIL WORKS, i.e., CONCRETE-ENCASED PVC UNDERGROUND DUCTS & FITTINGS, TO BE PRIMARY PROVIDED AND INSTALLED BY CABLES THE APPLICANT/CUSTOMER ELBOW ARRESTER PADMOUNTED TRANSFORMER TRANSFORMER VAULT TO BE CONSTRUCTED BY THE APPLICANT/CUST
Slide 6: Single Line Diagram - 2 Banks w/ 4-Way Junction
34.5 kV OH Line Lightning Fuse Cut-Out Arrester or Power Fuse 4-Way Loadbreak Junction, 200A Transformer Vault PRIMARY Vault Elbow Type Arrester DT's (SEE SECONDARY NOTE) Load Load Single Line Diagram - 2 Banks w/ 4-Way Junction
Slide 7: 4-Way / 4-Point Junction
MERALCO CORPORATE POWER UP FOR UM SERIES 4-WAY / 4-POINT JUNCTION
Slide 8: Transformers for Vault Installation: Padmounted
Transformers for Vault Installation Meralco-Supplied Padmounted Transformers Three-phase, 34.5 GrdY/20 kV or 13.2 GrdY/7.62 kV Available in either 240Y/139-V secondary (75-1000 kVA) or 480Y/277-V secondary (500-2000 kVA) 416Y/240 V secondary (500-1000 kVA)
Slide 9: Transformers for Vault Installation: Padmounted Features
Transformers for Vault Installation Meralco-Supplied Padmounted Transformers Deadfront primary Less flammable liquid filled Completely self- protected with fuses Provided with loop sectionalizing switch
Slide 10: Transformers for Vault Installation: Deadfront Distribution
Transformers for Vault Installation Meralco-Supplied Deadfront Distribution Transformer Single-phase, 34.5 GrdY/20 kV or 13.2 GrdY/7.62 kV Available in either 139/277-V secondary or 240/120-V secondary Available in 167 – 333 kVA
Slide 11: Transformers for Vault Installation: Deadfront Features
Transformers for Vault Installation Meralco-Supplied Deadfront Distribution Transformer Deadfront primary Round tank construction Less flammable liquid filled Provided with standard DT accessories
Slide 12: Standard Vault Location
Standard Vault Location
Slide 13: Preferred Vault Location
PREFERRED VAULT LOCATION: • PREFERRED VAULT LOCATION SHALL BE ON THE GROUND FLOOR • SECOND FLOOR MAY BE ALLOWED (FOR VAULT TYPE DT’s AND PADMOUNTED XF WITH HOISTING FACILITIES) • FIRST BASEMENT MAY BE ALLOWED FOR BUILDINGS WITH MULTIPLE BASEMENT
Slide 14: Preferred Vault Location
PREFERRED VAULT LOCATION: • THE VAULT SHALL BE LOCATED ON PERIMETER OF THE BUILDING • ADJACENT TO STREET/ROADWAY ACCESSIBLE TO MERALCO TRUCKS AND CRANE TRUCK MINIMUM ROAD WIDTH : 6.5 METERS
Slide 15: Standard Vault Specifications/Requirements
Standard Vault Specifications/Requirements
Slide 16: Standard Specification/Requirements
STANDARD SPECIFICATION/ REQUIREMENTS: • WALLS AND ROOF SHALL BE MADE OF REINFORCED CONCRETE NOT LESS THAN 150MM • THERE SHALL BE NO OPENING FROM THE VAULT TO ANY PART OF THE BUILDING INTERIOR • 150 MM DOORSILL IS REQUIRED FOR LIQUID CONFINEMENT • PROVISION FOR ADEQUATE AND PERMANENT VENTILATION (EXH
Slide 17: Standard Specification/Requirements
STANDARD SPECIFICATION/ REQUIREMENTS: • DUCTS (PRIMARY AND SECONDARY) – 110 MM DIAMETER, THICK WALLED, RED ORANGE COLOR, UNPLASTICIZED POLYVINYL CHLORIDE (UPVC) IN ACCORDANCE WITH PNS 14. IT SHOULD BE ENCASED IN CONCRETE • PROVISION OF PERSONNEL ACCESS DOORWAY DIRECTLY ACCESSIBLE FROM OUTSIDE OF THE
Slide 18: Customer Vault Layouts for Transformers
Customer Vault Layouts for Transformers (pdt & vt)
Slide 19: Requirements for Customer Vault: Padmount Transformers
Requirements for Customer Vault MINIMUM DIMENSION PADMOUNT TRANSFORMER IN VAULT LOCATION 1-BANK 2-BANKS (W) 5m X (D) 4m (W) 8m X (D) 4m Ground Floor X (H) 3m X (H) 3m (W) 5m X (D) 6m (W) 8m X (D) 6m 2nd Floor X (H) 4m* X (H) 4m* (W) 5m X (D) 6m (W) 8m X (D) 6m 1st Basement X (H) 3m X (H) 3m NOTES: [
Slide 20: Requirements for Customer Vault: Deadfront Transformers
Requirements for Customer Vault MINIMUM DIMENSION DEADFRONT (VAULT TYPE) DISTRIBUTION TRANSFORMERS LOCATION 1-BANK 2-BANKS (W) 5m X (D) 4m (W) 6m X (D) 6m Ground Floor x (H) 3m X (H) 3m (W) 5m X (D) 4m (W) 6m X (D) 6m 2nd Floor x (H) 3m X (H) 3m (W) 5m X (D) 4m (W) 6m X (D) 6m 1st Basement x (H) 3m
Slide 21: Primary Metering
PRIMARY METERING
Slide 22: Single Line Diagram for Primary Metering (OH)
SINGLE LINE DIAGRAM FOR PRIMARY METERING (OH)
Slide 23: Single Line Diagram for Primary Metering (UG)
SINGLE LINE DIAGRAM FOR PRIMARY METERING (UG)
Slide 24: Typical Primary Metering Arrangement
TYPICAL PRIMARY METERING ARRANGEMENT
Slide 25: MERALCO CORPORAT!
MERALCO CORPORAT! POWER UP FOR UM S ER
Slide 26: 3 Way RMU with Metering Module
3 Way RMU with Metering Module
Slide 27: 3 Way RMU with Metering Module
3 Way RMU with Metering Module
Slide 28: Thank you.
POWER UP FOR UM S ERIE S Thank you.