  1. Slide 1: MERALCO Standards: Electrical Design

    MERALCO Standards: Electrical Design Engr. Eduard Mercado Electrical Design Team

  2. Slide 2: Electrical Design Standards

    Electrical Design Standards

  3. Slide 3: Service Voltages and Facilities

    SERVICE VOLTAGES • SECONDARY METERED - 240 V, 400 V, 460 V • PRIMARY METERING -34.5 kV, 13.8 kV (portions of Cavite & Bulacan), 115 kV (Subtransmission) FACILITIES 1. OVERHEAD • POLE MOUNTED TRANSFORMERS • PADMOUNT TRANSFORMERS • VAULT TYPE DT 2. UNDERGROUND • PADMOUNT TRANSFORMERS • VAULT TYPE DT

  4. Slide 4: Single Line Diagram: Overhead Line Feeding a Transformer Vault

    Single Line INCOMING OVERHEAD LINE Diagram TERMINAL SURGE POLE ARRESTER FUSE CUTOUT OR POWER FUSE CABLE ALL CIVIL WORKS, i.e., TERMINATION CONCRETE-ENCASED PVC DUCTS & FITTINGS, TO BE UNDERGROUND PROVIDED AND INSTALLED BY PRIMARY THE APPLICANT/CUSTOMER CABLES ELBOW ARRESTER PADMOUNTED TRANSFORMER VA

  5. Slide 5: Single Line Diagram: Underground Feeder

    Single Line UNDERGROUND FEEDER Diagram PADMOUNTED SWITCHGEAR ALL CIVIL WORKS, i.e., CONCRETE-ENCASED PVC UNDERGROUND DUCTS & FITTINGS, TO BE PRIMARY PROVIDED AND INSTALLED BY CABLES THE APPLICANT/CUSTOMER ELBOW ARRESTER PADMOUNTED TRANSFORMER TRANSFORMER VAULT TO BE CONSTRUCTED BY THE APPLICANT/CUST

  6. Slide 6: Single Line Diagram - 2 Banks w/ 4-Way Junction

    34.5 kV OH Line Lightning Fuse Cut-Out Arrester or Power Fuse 4-Way Loadbreak Junction, 200A Transformer Vault PRIMARY Vault Elbow Type Arrester DT's (SEE SECONDARY NOTE) Load Load Single Line Diagram - 2 Banks w/ 4-Way Junction

  7. Slide 7: 4-Way / 4-Point Junction

    MERALCO CORPORATE POWER UP FOR UM SERIES 4-WAY / 4-POINT JUNCTION

  8. Slide 8: Transformers for Vault Installation: Padmounted

    Transformers for Vault Installation Meralco-Supplied Padmounted Transformers  Three-phase, 34.5 GrdY/20 kV or 13.2 GrdY/7.62 kV  Available in either 240Y/139-V secondary (75-1000 kVA) or 480Y/277-V secondary (500-2000 kVA)  416Y/240 V secondary (500-1000 kVA)

  9. Slide 9: Transformers for Vault Installation: Padmounted Features

    Transformers for Vault Installation Meralco-Supplied Padmounted Transformers  Deadfront primary  Less flammable liquid filled  Completely self- protected with fuses  Provided with loop sectionalizing switch

  10. Slide 10: Transformers for Vault Installation: Deadfront Distribution

    Transformers for Vault Installation Meralco-Supplied Deadfront Distribution Transformer  Single-phase, 34.5 GrdY/20 kV or 13.2 GrdY/7.62 kV  Available in either 139/277-V secondary or 240/120-V secondary  Available in 167 – 333 kVA

  11. Slide 11: Transformers for Vault Installation: Deadfront Features

    Transformers for Vault Installation Meralco-Supplied Deadfront Distribution Transformer  Deadfront primary  Round tank construction  Less flammable liquid filled  Provided with standard DT accessories

  12. Slide 12: Standard Vault Location

    Standard Vault Location

  13. Slide 13: Preferred Vault Location

    PREFERRED VAULT LOCATION: • PREFERRED VAULT LOCATION SHALL BE ON THE GROUND FLOOR • SECOND FLOOR MAY BE ALLOWED (FOR VAULT TYPE DT’s AND PADMOUNTED XF WITH HOISTING FACILITIES) • FIRST BASEMENT MAY BE ALLOWED FOR BUILDINGS WITH MULTIPLE BASEMENT

  14. Slide 14: Preferred Vault Location

    PREFERRED VAULT LOCATION: • THE VAULT SHALL BE LOCATED ON PERIMETER OF THE BUILDING • ADJACENT TO STREET/ROADWAY ACCESSIBLE TO MERALCO TRUCKS AND CRANE TRUCK MINIMUM ROAD WIDTH : 6.5 METERS

  15. Slide 15: Standard Vault Specifications/Requirements

    Standard Vault Specifications/Requirements

  16. Slide 16: Standard Specification/Requirements

    STANDARD SPECIFICATION/ REQUIREMENTS: • WALLS AND ROOF SHALL BE MADE OF REINFORCED CONCRETE NOT LESS THAN 150MM • THERE SHALL BE NO OPENING FROM THE VAULT TO ANY PART OF THE BUILDING INTERIOR • 150 MM DOORSILL IS REQUIRED FOR LIQUID CONFINEMENT • PROVISION FOR ADEQUATE AND PERMANENT VENTILATION (EXH

  17. Slide 17: Standard Specification/Requirements

    STANDARD SPECIFICATION/ REQUIREMENTS: • DUCTS (PRIMARY AND SECONDARY) – 110 MM DIAMETER, THICK WALLED, RED ORANGE COLOR, UNPLASTICIZED POLYVINYL CHLORIDE (UPVC) IN ACCORDANCE WITH PNS 14. IT SHOULD BE ENCASED IN CONCRETE • PROVISION OF PERSONNEL ACCESS DOORWAY DIRECTLY ACCESSIBLE FROM OUTSIDE OF THE

  18. Slide 18: Customer Vault Layouts for Transformers

    Customer Vault Layouts for Transformers (pdt & vt)

  19. Slide 19: Requirements for Customer Vault: Padmount Transformers

    Requirements for Customer Vault MINIMUM DIMENSION PADMOUNT TRANSFORMER IN VAULT LOCATION 1-BANK 2-BANKS (W) 5m X (D) 4m (W) 8m X (D) 4m Ground Floor X (H) 3m X (H) 3m (W) 5m X (D) 6m (W) 8m X (D) 6m 2nd Floor X (H) 4m* X (H) 4m* (W) 5m X (D) 6m (W) 8m X (D) 6m 1st Basement X (H) 3m X (H) 3m NOTES: [

  20. Slide 20: Requirements for Customer Vault: Deadfront Transformers

    Requirements for Customer Vault MINIMUM DIMENSION DEADFRONT (VAULT TYPE) DISTRIBUTION TRANSFORMERS LOCATION 1-BANK 2-BANKS (W) 5m X (D) 4m (W) 6m X (D) 6m Ground Floor x (H) 3m X (H) 3m (W) 5m X (D) 4m (W) 6m X (D) 6m 2nd Floor x (H) 3m X (H) 3m (W) 5m X (D) 4m (W) 6m X (D) 6m 1st Basement x (H) 3m

  21. Slide 21: Primary Metering

    PRIMARY METERING

  22. Slide 22: Single Line Diagram for Primary Metering (OH)

    SINGLE LINE DIAGRAM FOR PRIMARY METERING (OH)

  23. Slide 23: Single Line Diagram for Primary Metering (UG)

    SINGLE LINE DIAGRAM FOR PRIMARY METERING (UG)

  24. Slide 24: Typical Primary Metering Arrangement

    TYPICAL PRIMARY METERING ARRANGEMENT

  25. Slide 25: MERALCO CORPORAT!

    MERALCO CORPORAT! POWER UP FOR UM S ER

  26. Slide 26: 3 Way RMU with Metering Module

    3 Way RMU with Metering Module

  27. Slide 27: 3 Way RMU with Metering Module

    3 Way RMU with Metering Module

  28. Slide 28: Thank you.

    POWER UP FOR UM S ERIE S Thank you.